I have been using an 18V power supply while my robot was on the testing bench and all was well. When I attached the robot to its battery supply for fields testing the fuse blew to the motor controller as soon as it started up. I understand the surge current issue, but shouldn't it have blown when using the power supply also? Why does this happen? Any suggestions on how to fix this problem?
-
It's maybe your power supply can not deliver high current... cause batteries usually can...
Get a bigger fuse and test.... :)
-
Most benchtop power supplies max out at 1 or 2 amps. Your battery was probably giving out a lot more.
A fuse blows based on current.